    Anyone know what is the formula for sizing the line side of a power supply?
    Thanks,
  2. #2
    Join Date
    May 2003
    Leesburg, VA
    Posts
    7,072
    Unless I misread your post..........WOW, now that is a open question.
    Brian John
    Leesburg, VA
  3. #3
    Join Date
    Jan 2004
    Right here.
    Posts
    12,326
    Multiply by Pi.
  4. #4
    Join Date
    Dec 2006
    Eastern Oregon
    Posts
    3,504
    Quote Originally Posted by mdshunk
    Multiply by Cow Pi.
    Yep.:wink:
  5. #5
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    22,758
    Multiply by Pi.
    Quote Originally Posted by Cow
    Multiply by Cow Pi.
    What's wrong with this picture? :-?
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  6. #6
    Join Date
    Jan 2004
    Right here.
    Posts
    12,326
    Quote Originally Posted by LarryFine
    Larry Fine for President!
    I'm not sure.
  7. #7
    Join Date
    Nov 2007
    Posts
    8
    e.g. power supply is 115vac to 24vdc and it is a 10amp power supply.
    What size fuse is the line side (115vac)?
  8. #8
    Join Date
    Apr 2008
    Ann Arbor, Michigan
    Posts
    6,776
    080825-1039 EST
    CrazyCowPie:
    There are many factors.
    What do you want to protect? The load, the rectifiers, or the transformer?
    Inherently you have an inrush problem even with no load on the power supply. This might be the primary criteria because it may size the fuse larger than needed for the load. If you use a series input thermistor you can greatly reduce the peak inrush current and therefore more closely size the fuse to the load. Still you may want to use a slow-blow fuse.
    You need to take measurements. If the power supply will be fully loaded, then you certainly need more than a 2 A fuse just for the load and losses.
  9. #9
    Join Date
    Jan 2008
    Posts
    181
    Have you checked with the MFR?
    Most low voltage power supplies have a MFR, check the internet for a specifications sheet. Note: most 10A 24 VDC PS's have nearly the same fusing requirements. Example....
    http://web1.automationdirect.com/sta...s/rhinopsm.pdf
    If you can't find your MFR's spec sheet, cheat, reference 2 or 3 other MFR's spec sheets, the input fusing requirements should be pretty close for a given size ( amp load ). Don't forget to include your loads inrush current... Oh if your the MFR its back to measuring for a given load.. ( ie bench testing )
  10. #10
    Join Date
    Apr 2008
    Ann Arbor, Michigan
    Posts
    6,776
    080825-1342 EST
    CrazyCowPie:
    Another question:
    Is this a switching power supply or an ordinary transformer-rectifier supply?
    A switching supply is primarily a bridge rectifier feeding a capacitor input filter with some current limiting impedance for control of inrush current. Whereas a transformer-rectifier-capacitor supply has the added inrush from the transformer.
    To determine transformer inrush current you need to create special test circuitry, or experimentally run many trials to determine the peak value.
    To answer your first post I would suggest that there is not a simple formula to determine the sizing of the fuse.