Page 1 of 2 12 LastLast
Results 1 to 10 of 11
Thread: Formula for kW -> amps
  1. #1
    Join Date
    Sep 2008
    Posts
    2
    This is probably easy for you folks, just not me:
    Could someone provide the formula to calculate the amperage rating for a given load when the power source is known?
    I hope I've asked that right. My exact need is the amp rating for a 45 kW load on 208VAC 3-phase power.
    Thank you
  2. #2
    Join Date
    Feb 2006
    Pa.
    Posts
    2,021
    The multiplier for 3-phase 208 volt is 360. (208x1.73). 45000/360=125
  3. #3
    Join Date
    Jan 2008
    NC & IN
    Posts
    3,380
    If it's a continuous load add 1.25% to what ruwired said.
  4. #4
    Join Date
    Aug 2008
    San Francisco
    Posts
    677
    Exclamation Power Formula
    I googled it since my mind is gone..
    KW = KV X Amps X PF X 1.73 so assuming 0.8 power factor:
    45KW = 0.208KV X Amps X 0.8 X 1.73
    Amps = 45 / .208 X .8 x 1.73
    Amps = 45 / .2879
    Amps = 156.3A
    ? someone pls check this
    Am I in shape?? I get plenty of exercise pushing my luck!!
  5. #5
    Join Date
    Feb 2003
    Fl
    Posts
    17,095
    Quote Originally Posted by tonytonon
    See Ricks post.
    Roger
    Join Date
    Jul 2006
    Posts
    7,644
    Amps = 45 / .2879
    Amps = 156.3A
    This is close enough if it is a motor or other inductive load, also a safe bet if it is a mixed load. If it is a purely resistive load, i.e. heating elements or incandescent lights, then the power factor is unnecessary. But few loads are purely resistive.
  7. #7
    Join Date
    Feb 2003
    Wisconsin
    Posts
    9,855
    Quote Originally Posted by Jraef
    I agree, just don't convert HP straight to KW.
    Just because you can, doesn't mean you should.
  8. #8
    Join Date
    Sep 2008
    Posts
    2
    Thank you all.
    The load is an FM broadcast tube-type transmitter. The mftr is calling for a 250A FUSED disconnect, which seemed high.
    I guess that leads to this question then: Does the use of fuses require an increase in the disconnect's amp rating?
  9. #9
    Join Date
    Sep 2008
    UK
    Posts
    11,240
    Quote Originally Posted by jim dungar
    I don't follow you.
    In what circumstances would the conversion be the wrong thing to do?
  10. #10
    Join Date
    Feb 2003
    Wisconsin
    Posts
    9,855
    Quote Originally Posted by Besoeker
    I don't follow you.
    When many people try to determine the input KW of a motor which is rated in output HP, by simply converting HP to KW, they forget to account for the efficiency of the motor.