What is the intent of NEC 210.7(B)? We have a local official attempting to use this rule for a 3 Circuit Systems Furniture application.
What is the intent of NEC 210.7(B)? We have a local official attempting to use this rule for a 3 Circuit Systems Furniture application.
210.4(B) or 210.7(B)? Your post has one, your heading the other.Originally Posted by Jeff in Sacramento
Are you under the '08?
And also take a look at 605.6 and 605.7
John from Baltimore
"One Day at a Time"
Responses based on the 2008 NEC
If you can stay calm, while all around you is chaos...then you probably haven't completely understood the seriousness of the situation
I assume you mean 210.7(B) but your post title states 210.4(B).Originally Posted by Jeff in Sacramento
If you have 2 circuits that land on a device then you must use a dp breaker. If you are using MWBC then you have to use a 2p or 3p breaker anyway.
The intent is to protect someone from pulling out a recep. that was assumed disconnected because one side of the recep. was dead. If they were on 2 separate sp breakers then there is a possible of shock or shorting the circuit.
Multiwired branch circuits feeding furniture systems required a commom trip starting in 2005.Originally Posted by JohnJ0906
Rick