Master bathroom whirlpool/jacuzzi tub

Status
Not open for further replies.

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
In my area, depends on the tub. Normally not, but on occasion the mfg. install calls for such bond in the install instructions. (see attached Jacuzzi View attachment 2664 instruction)
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
In my area, depends on the tub. Normally not, but on occasion the mfg. install calls for such bond in the install instructions. (see attached Jacuzzi View attachment 2664 instruction)

And this just proves that the manufacturers have no idea of what they are requiring. It is never required to bond a #8 back to a panel for a hot tub, pool, or hydromassage tub. It irks me to no end how the mfg. are allowed to require ridiculous installations instructions.
 

acrwc10

Master Code Professional
Location
CA
Occupation
Building inspector
Usually it is a #8 to the cold water suppling the tub, and the circuit it is plugged into has it's ground also, done. Assuming all metal piping in the house.
 