Results 1 to 6 of 6
Thread: Metal Halide and Merc Vapor Compatability
  1. #1
    Join Date
    Sep 2005
    Currently in NJ
    Posts
    865
    Had a disagreement with a co-worker yesterday. Through research I have found that mercury vapor bulbs can be used in metal halide fixtures but a metal halide bulb cannot be used in a mercury vapor fixture. Co-worker says that's hog wash and knows a number of electricians that use MH bulbs in a MV fixture with supposedly good results. Who's right here?
  2. #2
    Join Date
    Jul 2008
    Lake Ridge, VA
    Posts
    1,794
    Quote Originally Posted by mark32 View Post
    I don't know the answer to that one, but have often wondered if they were compatible with one another. I'm sure you'll get plenty of answers here in a couple of minutes.
  3. #3
    Join Date
    Feb 2006
    new york
    Posts
    4,258
    If my memory serves me correct I believe one needs a starter (hv pulse) and one doesnt. I think that you are correct as to which is which. I believe that the more modern lamps are Multi Vapor and this may be why these lamps start in both fixtures.
    The tail does NOT wag the dog.
  4. #4
    Join Date
    Jul 2006
    Posts
    7,157
    Quote Originally Posted by quogueelectric View Post
    Yes and no. All MH lamps 150W and under need a (relatively) high voltage starting pulse. MV does not. So you can put a MV lamp into a MH fixture (why you would want to, I don't know...) but if you put a <150W MH lamp into an older MV fixture, the ballast system will not have that pulse start and will fail to strike the initial arc necessary for the MH lamp. In the past, MH lamps over 150W had a different starting system and could possibly work without the pulse, but in recent years the lamp mfrs have determined that pulse start works better for all sizes and have been shifting that way. So it may have been true that in the past if you were replacing a 400W MV lamp with a 400W MH lamp it would work, but depending on the lamp that may no longer be true.
    The "multi vapor" lamps that GE is selling are meant as universal donors with HPS, not MV, but mainly it is just a "marketing term" for GE's latest and greatest MH improvement. They can be used in virtually any burning position and fixture design, but it is definitely a pulse start lamp, so it ill NOT work in MV fixtures..
  5. #5
    Join Date
    Jul 2007
    Iowegia
    Posts
    17,691
    From Advance Transformers Troubleshooting guide to HID:
  6. #6
    Join Date
    Mar 2003
    Nord'est Wisconsin et Paris France
    Posts
    1,026
    Interchangeable can be done between the MV and MH { probe start only } but in warm and hot day it will have no issue to get it lit up but in cold days that where it show up.
    The probe start MH will not start with MV gear in there due the OCV and running voltage in the system.
    However with instering twist yeah you can stick in MV bulb in Probe start MH gear and have no side effect exept you know how bright those MV bulb dish out no diffrence at all.
    From my past experince that useally a #1 curpit for me in cold area and also there are some lumianire that they are not approved to use the MH bulb for safety reason. { this is true on <250 w unless it have open bottom rated bulb }
    Merci,Marc
    Marc
    master electrician
    Wisconsin and Paris France
    "Pas de problème, il marche n'est-ce pas?" (No problem, it works doesn't it?)
Posting Permissions
  • You may not post replies
  • You may not edit your posts