Moduler Furniture?

Status
Not open for further replies.

The Iceman

Senior Member
Location
Florida
I'm wiring up some moduler furniture (cubicles) in an office tomorrow. The pre-wired flex has three circuits feeding each module. I thought in the 2005 NEC their is a code that says these three circuits must be terminated on a three pole circuit breaker, or be able to simultaneously disconnect all ungrounded conductors with aproved handle-ties. I can't seem to find it, or maybe I'm wrong. Any help would be greatly appreciated.
 

Buck Parrish

Senior Member
Location
NC & IN
I'm wiring up some moduler furniture (cubicles) in an office tomorrow. The pre-wired flex has three circuits feeding each module. I thought in the 2005 NEC their is a code that says these three circuits must be terminated on a three pole circuit breaker, or be able to simultaneously disconnect all ungrounded conductors with aproved handle-ties. I can't seem to find it, or maybe I'm wrong. Any help would be greatly appreciated.

I could be wrong, but I am pretty sure it is in the 08 book. The 05 code required handle ties for two circuits on the same yoke.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
I'm wiring up some moduler furniture (cubicles) in an office tomorrow. The pre-wired flex has three circuits feeding each module. I thought in the 2005 NEC their is a code that says these three circuits must be terminated on a three pole circuit breaker, or be able to simultaneously disconnect all ungrounded conductors with aproved handle-ties. I can't seem to find it, or maybe I'm wrong. Any help would be greatly appreciated.

Yes, If the three circuits are a multiwire branch circuit. Take a look at 605.6 for fixed partitions and 605.7 for free-standing type partitions.

Chris
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
This is in both the 2005 and 2008 NEC and was a code change that first appeared in the 2005 code.
 

raider1

Senior Member
Staff member
Location
Logan, Utah
This is in both the 2005 and 2008 NEC and was a code change that first appeared in the 2005 code.

Correct, though now that the 2008 NEC requires ALL multiwire branch circuits to have a simultaneous disconnecting means the sections in 605 are really not needed anymore.

Chris
 

The Iceman

Senior Member
Location
Florida
Yes, If the three circuits are a multiwire branch circuit. Take a look at 605.6 for fixed partitions and 605.7 for free-standing type partitions.

Chris

Thanks chris, I thought it was in there. I think they are multywire branch circuits for fixed partitions. I appreciate the help.
 