Originally Posted by
wbalsam1
I can see bonding the building steel to the service as is required,
but bonding the motor to building steel might have the effect of dividing a fault current between the equipment grounding conductor of the motor circuit and along the building steel
which might limit the current on the egc to the extent the OCPD would not open. What say you?
WBalsam,
The total of the available current
will flow through the total of the available conductors.
View the EGC as a conductor, and
view the building steel ground as a conductor.
The Voltage divides according to the conductance.
This action is parallel in these parallel conductors.
So, the lesser conductance of the building steel
only means that less current will flow through it.
The larger share will flow through the EGC.
The OCPD will trip if this total is sufficient.
A proper EGC will allow enough current to trip the OCPD, by itself,
without any help from an additional path (building steel).
Hope you enjoy the forum.
Comments are welcome.
...