    Is there a simple formula for determining the unbalanced neutral current in a 3p-4w system? I know how to calculate it if the line to neutral loads on two phases is equal and the line to neutral load on the third phase is different, but what if the line to neutral load is different on each phase?
    In other words, if I have a 3ph-4w 208/120v panelboard and connect three circuits, one on phase A, one on phase B, and one on phase C and the corresponding 120v loads are 10A on phase A, 8A on phase B, and 6A on phase C, what would my neutral current be from the unbalanced loads which are all 120 degrees out of phase?
  2. #2
    Join Date
    Feb 2003
    Fl
    Posts
    16,818
    Quote Originally Posted by stevee View Post
    SQRT (I^A + I^B + I^C) - (IA x IB) + (IB x IC) + (IC x IA)
    SQRT (10 x 10 + 8 x 8 + 6 x 6) - (10 x 8) + (8 x 6) + (6 x 10)
    SQRT (100 + 64 + 36) - (80) + (48) + (60)
    SQRT 200 - 188 = 12
    SQRT 12 = 3.46
    Roger
    Join Date
    Jul 2007
    Iowegia
    Posts
    17,701
    Two write it out a bit better, it's
    √((IaČ+IbČ+IbČ)-(Ia*Ib)-(Ib*Ic)-(Ia*Ic))
  4. #4
    Join Date
    Feb 2003
    Fl
    Posts
    16,818
    Quote Originally Posted by 480sparky View Post
    Why do you think it's better? Might it have something to do with symbols or two?
    Actually, I think one could do it fine.
    Roger
    Join Date
    Jul 2007
    Iowegia
    Posts
    17,701
    Quote Originally Posted by roger View Post
    Roger
    I^A means what? I (amps) to the power of A (?)
    Also, you don't have enough parentheses nested.
    Roger
    Appears you take the square root of the first set of parantheses, then start subtracting the other three sets.
  6. #6
    Join Date
    Feb 2003
    Fl
    Posts
    16,818
    Oooops, good point should have been I^2A etc...., but I still don't know why it takes two to write it a bit better. :wink:
    Roger
    Join Date
    Jul 2007
    Iowegia
    Posts
    17,701
    Roger
    That's the problem with such a formula. Writing it out with common computer keyboard symbols makes it difficult to follow the hierarchy of the formula.
    You did a good job explaining it on your first post, though.
    Are you asking why it takes two sets of parentheses? To force the Square-Root function to be the last. The way you originally wrote it, it would actually work out this way:
    SQRT (I^A + I^B + I^C) - (IA x IB) + (IB x IC) + (IC x IA) means the SQRT function would only apply to the first set of parentheses. You'd end up with:
    SQRT (10*10 + 8*8 + 6*6) - (10*8) + (8*6) + (6*10)
    SQRT (200) - (188)
    At this point, the SQRT function only would aply to the 200, so you end up with
    14.14 - 188 = -185.86.
    It's kinda of difficult to have a negative amperage flow. :smile:
    At least, this is how I remember it from school, back when dirt was invented.
    Edit to add: I just noticed my first formula was wrong. I had IbČ in the first set of parenthesis twice. It should be:
    √((IaČ+IbČ+IcČ)-(Ia*Ib)-(Ib*Ic)-(Ia*Ic))
    And to be hard on myself, I should also add the following variables explained:
    Ia = Amp flow on phase A
    Ib = Amp flow on phase B
    Ic = Amp flow on phase C
  8. #8
    Join Date
    Feb 2003
    Fl
    Posts
    16,818
    No, I'm asking why you say Two write it out a bit better. Even though I was in a hurry and answering phone calls while I was posting, I think One (even if just myself) can write it out correctly.
    Hint, read the first sentence of your first post. :wink:
    Roger
    Join Date
    Jul 2007
    Iowegia
    Posts
    17,701
    Roger
    OOOOOOOOOOoooooooooooo! Sea watt hapens wen theirs know SpellCheck?
  10. #10
    Join Date
    Feb 2003
    Fl
    Posts
    16,818
    If you're like me and are doing anything else or are the least little bit preoccupied, things do get missed and typo's do happen.
    Roger