    Can we get a Chicago plenum rated 2x4 fixture which has emergency fluorescent battery inverter - to be used as emergency lighting?
  2. #2
    Join Date
    Nov 2006
    Pinellas County, FL
    Posts
    1,468
    I am not familiar with "Chicago". I would say taking the chicago portion out of your post, my answer would initially be yes.
    ____________________________
  3. #3
    Join Date
    Aug 2003
    Chicago, IL
    Posts
    92
    In 18-27-700.6 (b) "Emergency lighting systems shall be designed and installed so that the failure of any individual lighting element, such as the burning out of a light bulb, cannot leave in total darkness any space that requires emergency illumination."
    Typical emergency lights are the frog eye type battery backup that are either wall or cieling mounted. I would think this is the reason. With a flourescent fixture, the battery backup is typically either the inside 2 or outside 2 lamps. If one of these lamps burns out, you will be left in total darkness.
  4. #4
    Join Date
    Mar 2004
    Arizona
    Posts
    3,913
    Quote Originally Posted by esox39 View Post
    If more than one fixture is in an area then, imo, there would not be total darkness.
    Frank Arizona,USA
  5. #5
    Join Date
    Mar 2004
    Arizona
    Posts
    3,913
    A google search found ' Chicago plenum fixture", it basicly limits the air flow from room
    side to the plenum. FYI.
    Frank Arizona,USA
  6. #6
    Join Date
    Feb 2003
    Burbank IL
    Posts
    982
    I don't know if there is a Chicago approved plenum rated fluorescent lay in fixture, with emergency backup supply.
    I didn't see one on Cooper Lighting's web site, although they had a NY approved one.
    Russ Burbank IL