Can a load center be installed in a bathroom of an accessory building? accessory building is detached from a dwelling unit.

240.24(E) may or may not apply
 

LEO2854

Esteemed Member
Location
Ma
Can a load center be installed in a bathroom of an accessory building? accessory building is detached from a dwelling unit.

240.24(E) may or may not apply

What is the building used for?


Article 100.....Dwelling Unit. A single unit, providing complete and independent living facilities for one or more persons, including permanent provisions for living, sleeping, cooking, and sanitation.


Building. A structure that stands alone or that is cut off from adjoining structures by fire walls with all openings therein protected by approved fire doors.


Bathroom. An area including a basin with one or more of the following: a toilet, a urinal, a tub, a shower, a bidet, or similar plumbing fixtures.


240.24(E) Not Located in Bathrooms. In dwelling units, dormitories, and guest rooms or guest suites, overcurrent devices, other than supplementary overcurrent protection, shall not be located in bathrooms.
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
What is the building used for?

It is a detached structure from the house. It is not being used as a living space. It can be a garage, work shop, office, storage shed, pool house ........... it can be used for any purpose except as as a living space that happens to have a bathroom.
 

kwired

Electron manager
Location
NE Nebraska
240.24(E) Not Located in Bathrooms. In dwelling units, dormitories, and guest rooms or guest suites, overcurrent devices, other than supplementary overcurrent protection, shall not be located in bathrooms.

This space is not a dwelling unit, dormitory or guest room/ guest suite. Nothing prohibits the OP's situation. Just because the property has a dwelling unit on it does not make all of the property a dwelling unit.
 

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
True, but sometimes we want it both ways. Can you use exposed NM cable in that detached building without a 15 minute flash barrier? Most inspectors let you do that if it was on residential property, but the code did not. Finally the code was modified to explicitly allow this. There are probably other things only allowed in dwellings that we'd want to be able to do in an accessory building too, I just can't think of any more...

I'd check your local authorities to see how they treat accessory buildings to dwellings. However, I don't know why the code would be OK with a panel in a commercial bathroom, but not a residential one.
 