Page 1 of 4 123 ... LastLast
Results 1 to 10 of 32
Thread: what is MCM?
  1. #1
    Join Date
    Jan 2009
    Posts
    3
    what is MCM?
    I'm looking at a set of plans where it is proposed to install 4-500 MCM THHN CU conductors in a 3 -1/2" conduit, which I presume will be RMC. I'm familiar with AWG and KCMIL, but MCM is new to me.
  2. #2
    Join Date
    Feb 2003
    Seattle, WA
    Posts
    18,783
    MCM is precisely the same as KCMIL. It is the older version. I believe the initial "M" comes from the Roman numeral that represents 1000. Some have said that it comes from the French word, "Mille," which also means 1000.
    Welcome to the forum.
    Charles E. Beck, P.E., Seattle
    Comments based on 2017 NEC unless otherwise noted.
  3. #3
    Join Date
    Jan 2009
    Posts
    3
    Thanks Charlie B
    That's what I suspected, but thought I'd better be sure.
  4. #4
    Join Date
    Feb 2003
    Indianapolis
    Posts
    6,102
    Thumbs down I am getting old!
    I can't believe kcmil has been around so long that some people do not know what MCM means. This is a mix of Roman Numerals and abbreviations, M = 1000, C = circular, and the second M = mils (0.001 diameter). I am getting old right before my eyes! :rolleyes:
    Charlie Eldridge, Indianapolis, Utility Power Guy
    Responses based on the 2011 NEC, unless stated otherwise.
  5. #5
    Join Date
    Jul 2007
    Iowegia
    Posts
    17,747
    Quote Originally Posted by charlie View Post
    If it makes you feel better, T310.16 used MCM up through the '87. In the '90, it was changed to KCMIL.
  6. #6
    Join Date
    May 2005
    Barboursville, West Virginia
    Posts
    895
    Quote Originally Posted by 480sparky View Post
    In '87 I was in the 2nd grade. By '90, I had made it all the way to 5th grade. If it didn't have to do with Legos or Transformers (the robots, not the electromagnetic devices) I didn't care about it. However, the wire manufacturer that I worked for up until mid-November used MCM even more than kcmil, so I don't have any problem with either of them.
  7. #7
    Join Date
    Feb 2003
    Germantown MD
    Posts
    755
    It makes me feel old and I am only 29. It took me time to get MCM out of my head, and get use to Kcmills.
    Make something idiot proof and someone will make a better idiot.
  8. #8
    Join Date
    Jul 2007
    Iowegia
    Posts
    17,747
    Quote Originally Posted by mikeames View Post
    Now you need to let loose of 'fixture' and substitute 'luminaire'.
  9. #9
    Join Date
    Feb 2003
    Germantown MD
    Posts
    755
    Probably not going to happen but some one nailed me one time when I called a 8 foot t-12 lamp a "bulb" so now when I discuss lamps and bulbs I stop to think who I am talking to. If I am talking to a tradesman then I use the correct name. If it anyone else then I call everything (HID lamps, flourescent lamps, or an A19 bulb) light bulbs so I don't confuse them.
    I need to go re-lamp some 'luminaires'
  10. #10
    Join Date
    May 2003
    Leesburg, VA
    Posts
    7,069
    That I had not heard INTERESTING.
    Brian John
    Leesburg, VA
Posting Permissions
  • You may not post replies
  • You may not edit your posts