What size wire do you run for a receptacle 150ft from the panel?
this would just be a general plug in a commercial building

If you have more than one receptacle on the circuit do you upsize the wire to the last receptacle or just to the first one?

most of the time we up size from #12 to # 10 around 100ft.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Really depends on the potential load. If the load is expected to be very small you may not need any increase in conductor size.
 