What size wire do you run for a receptacle 150ft from the panel?
this would just be a general plug in a commercial building
If you have more than one receptacle on the circuit do you upsize the wire to the last receptacle or just to the first one?
most of the time we up size from #12 to # 10 around 100ft.
this would just be a general plug in a commercial building
If you have more than one receptacle on the circuit do you upsize the wire to the last receptacle or just to the first one?
most of the time we up size from #12 to # 10 around 100ft.