not sure...

Status
Not open for further replies.

panhandle444

Member
Location
oklahoma
Please point out issues and let me know if this is right. I'm still learning.

A recessed light is located within three feet of an opening in a class 1 division 2 location. A seal off is installed within 18" of the fixture. From the seal off liquidtight is ran to a four square located outside the classified area. Is a seal off required at the end of the liquidtight before the four inch square?



Thx
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
Can't quite tell from your description - is the luminare and its wiring actually in the classified location.
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
I apologize for my confusion, but if I understand your description correctly, the existing seal mentioned is acting a boundary seal; being within 18" of the luminaire is irrelevant and a seal at the four in square box is useless in any case.
 
Status
Not open for further replies.
Top