    Cable Size for Generator 100KVA

    I have existing generator with a capacity of 90KVA the cable size I used is 4x95 mm2, I decided to change 90 to 100 KVA, Can I still use the existing cable or should I upgrade the cable size?

    Thank you...

    May God Bless us all

    best regards,
    Eduardo
    Ed

  2. #2
    Join Date
    Mar 2005
    Location
    California
    Posts
    1,973
    What's the breaker size (OCPD)?

    See 445.12(A) & 445.13

  3. #3
    Join Date
    Sep 2008
    Location
    UK
    Posts
    6,346
    Quote Originally Posted by Eduardo Maun View Post
    I have existing generator with a capacity of 90KVA the cable size I used is 4x95 mm2, I decided to change 90 to 100 KVA, Can I still use the existing cable or should I upgrade the cable size?

    Thank you...

    May God Bless us all

    best regards,
    Eduardo
    A few questions......
    Which country and what standards/codes apply?
    What voltage is the generator?
    Single core cables?
    Armoured/unarmoured?
    Method of installation?
    Last edited by Besoeker; 03-07-09 at 11:07 AM.

  4. #4
    Join Date
    May 2006
    Location
    Qatar
    Posts
    62

    Generator Cable Size

    A few questions......
    Which country and what standards/codes apply? Qatar/Middle East
    What voltage is the generator? 415Vac
    Single core cables? 4C x 95 mm2
    Armoured/unarmoured? Armoured
    Method of installation? What is this?


    Thank you...

    God Bless...
    Ed

  5. #5
    Join Date
    May 2006
    Location
    Qatar
    Posts
    62

    Generator Cable Size

    What's the breaker size (OCPD)? - 200A
    Ed

  6. #6
    Join Date
    Mar 2008
    Location
    Abuja - Nigeria
    Posts
    37
    You don't need to upgrade the cable as long as the lenght does not exceed 600 feet
    We learn from our mistakes, that is why I'm getting a great education!

  7. #7
    Join Date
    Nov 2005
    Location
    Canterbury, New Zealand
    Posts
    1,877
    Quote Originally Posted by Eduardo Maun View Post
    Method of installation? What is this?
    Free air, clipped to wall, on cable tray, buried etc. Used to derate for heat buildup.

    Is this four single 95mm SWR cables or a four core SWR cable?

  8. #8
    Join Date
    Mar 2003
    Posts
    420
    you forgot laid out on the ground as single twisted strands of bailing wire with brown paper bags wrapped around it

  9. #9
    Join Date
    Nov 2005
    Location
    Canterbury, New Zealand
    Posts
    1,877
    I hate those sorts of jobs. There are brown paper bags and brown paper bags, and sometimes the derate tables are all wrong...

  10. #10
    Join Date
    Mar 2005
    Location
    California
    Posts
    1,973
    Quote Originally Posted by Eduardo Maun View Post
    What's the breaker size (OCPD)? - 200A
    Your cable or conductor size has to be compatible with this 200A