I want to install a two gang 100 amp meter base with disconnects for each can I run the feeder wires in the same conduit in to the building ? what code article ?
 

JoeStillman

Senior Member
Location
West Chester, PA
If the disconnects are outside with the meters, then the downstream circuits are feeders, not services. You just have to remember to derate for multiple current-carrying conductors.
 

kwired

Electron manager
Location
NE Nebraska
Are you dealing with multiple occupancies?

May not be acceptable in some of those instances to feed one occupant through another occupant space.

If you have a single occupancy with multiple meters there shouldn't be any problem.
 