Is the 800% allowable setting based on the actual motor FLA or the table FLA values?
al Senior Member Location Minnesota Apr 24, 2014 #1 Is the 800% allowable setting based on the actual motor FLA or the table FLA values?
david luchini Moderator Staff member Location Connecticut Occupation Engineer Apr 24, 2014 #2 al said: Is the 800% allowable setting based on the actual motor FLA or the table FLA values? Click to expand... Table FLA values
al said: Is the 800% allowable setting based on the actual motor FLA or the table FLA values? Click to expand... Table FLA values
T texie Senior Member Location Fort Collins, Colorado Occupation Electrician, Contractor, Inspector Apr 24, 2014 #3 al said: Is the 800% allowable setting based on the actual motor FLA or the table FLA values? Click to expand... Table values. See 430.6 for details. Also note requirement of 430.52(C)(3).
al said: Is the 800% allowable setting based on the actual motor FLA or the table FLA values? Click to expand... Table values. See 430.6 for details. Also note requirement of 430.52(C)(3).