For service calculations, when calcultaions the demand for a heat pump system, how is the heat pump load calculated for the situation of the comprossor and emergancy heat being energized at the same time
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
At most you only need 65% of the supplemental heat even if they aren't interlocked.

Same paragraph as Dennis mentioned.
 