cooper or aluminum EGC

Status
Not open for further replies.

tdjs

Member
I'm running an underground feeder[URD Alum.] from a service on a pole to a detached garage located 50 feet away.The inspector requires a copper EGC based on the 2008 NEC.Has anyone ran aluminum conductors for the EGC?This is in a rural area not ag. related[547].
 

charlie

Senior Member
Location
Indianapolis
I'm running an underground feeder [URD Alum.] . . . The inspector requires a copper EGC . . .
To get this started, URD cable is not recognized by the NEC but USE is acceptable to be used. There is no reason to require Cu. conductors unless you are planning to run the EGC as a bare wire. :smile:
 

JohnJ0906

Senior Member
Location
Baltimore, MD
I'm running an underground feeder[URD Alum.] from a service on a pole to a detached garage located 50 feet away.The inspector requires a copper EGC based on the 2008 NEC.Has anyone ran aluminum conductors for the EGC?This is in a rural area not ag. related[547].

Based on exactly what in the '08 NEC?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
While USE is code permitted, it is not permitted to enter a building even for termination purposes unless it has an additional rating that is one that is listed in Table 310.13.
 