2000 amp stand up board grounding question

Status
Not open for further replies.

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Yes 2 rods with a #6 to the rods. For 2000 amps you need to figure the circular mils of the service conductors and then look at T250.66. I am assuming you mean grounding electrode conductor
 