Default Underground junction box

I am trouble shooting some pole lights in a parking lot at a commercial retail center. There is an under ground junction box in the middle of one of the lanes and is full of wires that are spliced. The box is full of water and when we turn the breakers on you can hear the conductors arching under the water. Is there any way to replace this junction box and have it water tight?
  #2  
Old 04-30-2009, 08:20 PM
480sparky's Avatar
480sparky 480sparky is offline
Senior Member
 
Join Date: Jul 2007
Location: West of billsnuff
Posts: 14,766
Default

Quote:
Originally Posted by mitch cochrell View Post
...... Is there any way to replace this junction box and have it water tight?
Not really. Remake the connections with a water-tight system instead as water will always find it's way into an underground box.
__________________
All posts entered between 4:17 and 4:18 AM CDT will be worded to please Bob.
  #3  
Old 04-30-2009, 08:46 PM
SiddMartin SiddMartin is offline
Senior Member
 
Join Date: Feb 2008
Location: PA
Posts: 621
Default

Quote:
Originally Posted by 480sparky View Post
Not really. Remake the connections with a water-tight system instead as water will always find it's way into an underground box.
I agree, only way you can do it.
  #4  
Old 04-30-2009, 08:47 PM
ultramegabob's Avatar
ultramegabob ultramegabob is offline
Senior Member
 
Join Date: Mar 2008
Location: Indiana
Posts: 2,535
Default

I use gel filled wire nuts and then dip them in Plasti-coat...

http://www.plastidip.com/home_solutions/Plasti_Dip
__________________
THIS SPACE FOR RENT
  #5  
Old 04-30-2009, 08:52 PM
Jim W in Tampa's Avatar
Jim W in Tampa Jim W in Tampa is offline
Senior Member
 
Join Date: Mar 2006
Location: Tampa Florida
Posts: 6,942
Default

Lot of silicone and just redo every connection. Personally would solder them and shrink rap. Just no good way to make it last. Call it a design problem. Would been smarter to made splices within the poles at the covers.
  #6  
Old 04-30-2009, 08:53 PM
Twoskinsoneman's Avatar
Twoskinsoneman Twoskinsoneman is offline
Senior Member
 
Join Date: May 2007
Location: WV
Posts: 1,282
Default

Quote:
Originally Posted by Jim W in Tampa View Post
Lot of silicone and just redo every connection. Personally would solder them and shrink rap. Just no good way to make it last. Call it a design problem. Would been smarter to made splices within the poles at the covers.
shame on you
__________________
We will conquer land with water!
  #7  
Old 04-30-2009, 09:04 PM
ultramegabob's Avatar
ultramegabob ultramegabob is offline
Senior Member
 
Join Date: Mar 2008
Location: Indiana
Posts: 2,535
Default

also, you can use a wet/dry vac to get the water out of the box, sometimes it takes quite a bit of vacuuming to get all the water that is backed up into the conduits that keeps running into the box....
__________________
THIS SPACE FOR RENT
  #8  
Old 04-30-2009, 09:09 PM
Jim W in Tampa's Avatar
Jim W in Tampa Jim W in Tampa is offline
Senior Member
 
Join Date: Mar 2006
Location: Tampa Florida
Posts: 6,942
Default

Quote:
Originally Posted by ultramegabob View Post
also, you can use a wet/dry vac to get the water out of the box, sometimes it takes quite a bit of vacuuming to get all the water that is backed up into the conduits that keeps running into the box....
Then fix fast because water be back in few hours. Turn power off first or you might suck up electrons
  #9  
Old 04-30-2009, 09:24 PM
hillbilly1 hillbilly1 is offline
Senior Member
 
Join Date: Jul 2007
Posts: 1,281
Default

Your pretty much screwed down there with the high water table, when I come across one of these screw ups, I take the box out and replace it with an open bottom Quasite box. Set the quasite box on a deep bed of gravel to help drainage (will not work well were your at) seal connections as best as possible. I just got through fixing one that was buried almost three feet deep! Would not have know it was there, but logic dictated that's what someone had done, there was only one conduit out of the pole that was in the middle of a run.
  #10  
Old 04-30-2009, 11:07 PM
rt66electric rt66electric is offline
Senior Member
 
Join Date: Dec 2008
Posts: 217
Default make you lid tight

remember gradeschool science exp-- when you invert a glass and push it underwater,the air is trapped in the glass and remains air tight. the same is true in a UG box, either have a airproof lid, or place a inverted coffee can or such on top of the joints to keep the joints dry.. the water level may rise, but there is trapped air (and joints) under the plastic coffee can...:smile:
Closed Thread

CEU Banner Home Page

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -4. The time now is 06:43 AM.

- Archive - Top

Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.