Thread: Minimum burial depth for PVC

  1. #1
    Join Date
    Oct 2008
    Posts
    512

    Minimum burial depth for PVC

    What is the minimum burry depth for PVC conduit burried undergroud? I have seen a specification of 30" for a ductbank however this particular conduit will not be in a ductbank. Shoud there be at least 24" from grade to the PVC?

  2. #2
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    12,774
    It can range from 0" under a slab to 30" depending on the circuit. You need to check 300.5
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  3. #3
    Join Date
    Apr 2009
    Location
    Oregon Coast
    Posts
    507
    In the 2008 NEC, 352.10(G) (PVC Conduit section) refers you back to Table 300.5 (minimum cover requirements, 600V and less). The burial depth of the pipe will depend on what's above it. Table 300.5 Column 3 should give you the answer for PVC.
    We have clearance, Clarence. Roger, Roger. What's our vector, Victor?

  4. #4
    Join Date
    Mar 2009
    Posts
    203
    Quote Originally Posted by ericsherman37 View Post
    In the 2008 NEC, 352.10(G) (PVC Conduit section) refers you back to Table 300.5 (minimum cover requirements, 600V and less). The burial depth of the pipe will depend on what's above it. Table 300.5 Column 3 should give you the answer for PVC.
    The area I will be burying the conduit is on a grassy area beside a parking lot. Because I do not see anything covering a "field" or "grassy area" I believe that I should use the first row in this table for "all locations no specified below" and therefore burry it at least 18" deep

  5. #5
    Join Date
    Mar 2006
    Location
    Westchester County, New York
    Posts
    8,169
    Quote Originally Posted by PhaseShift View Post
    The area I will be burying the conduit is on a grassy area beside a parking lot. Because I do not see anything covering a "field" or "grassy area" I believe that I should use the first row in this table for "all locations no specified below" and therefore burry it at least 18" deep

    That is correct.
    Instructor, Industry Advocate

  6. #6
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    12,774
    field ?
    don't do like one fellow did me. That 18" is from the top of the dirt, not the top of the field grass
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  7. #7
    Join Date
    Feb 2005
    Location
    Wilmington, NC
    Posts
    4,497
    Quote Originally Posted by PhaseShift View Post
    ...and therefore burry it at least 18" deep
    A minor detail. It's 18" of cover, not 18" deep trench (I know you didn't say this).
    Lou (wannabe economist)

    If you relentlessly pursue perfection, you will eventually catch excellence.

  8. #8
    Join Date
    Aug 2006
    Location
    Miami Fla.
    Posts
    6,894
    Quote Originally Posted by hardworkingstiff View Post
    A minor detail. It's 18" of cover, not 18" deep trench (I know you didn't say this).
    Pool panel feeder, I go 20 inches to the top so there are no questions during inspection. Although getting a trench 2 inches deeper here is cake.


  9. #9
    Join Date
    Jul 2008
    Location
    Michigan
    Posts
    1,904
    Chris it's easy for you, you have Al.

  10. #10
    Join Date
    Jul 2004
    Location
    Louisville, Kentucky
    Posts
    1,941
    Quote Originally Posted by SEO View Post
    Chris it's easy for you, you have Al.
    Al is just about starting to catch up with Iwire's presents on this forum.
    Norb
    My Boss is a Tyrant and my Employee is an Idiot.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •