Default nominal voltage

Can anyone explain to me what is ment by nominal voltage? If you have a 120/240 service, is your nominal voltage the 120 legs to ground? or the 240? I do not understand how you can get 240 to ground. From what Ive read, the circuit is based on the equipment to be used. In other words, if you have 240volt heaters the circuit is considered 240v nominal yet what would be your reference point. You see nominal voltage all over the code book, I must have a thick head. Thanks
  #2  
Old 05-28-2009, 09:03 AM
480sparky's Avatar
480sparky 480sparky is offline
Senior Member
 
Join Date: Jul 2007
Location: West of billsnuff
Posts: 14,766
Default

From Art. 100:

Quote:
Voltage, Nominal. A nominal value assigned to a circuit or system for the purpose of conveniently designating its voltage class (e.g., 120/240 volts, 480Y/277 volts, 600 volts). The actual voltage at which a circuit operates can vary from the nominal within a range that permits satisfactory operation of equipment.
(blue highlight is mine)

It means a 240-volt circuit may not be exactly 240.00000 volts.
__________________
All posts entered between 4:17 and 4:18 AM CDT will be worded to please Bob.
  #3  
Old 05-28-2009, 09:20 AM
ray cyr ray cyr is offline
Member
 
Join Date: Jan 2007
Location: Yakima, Wash.
Posts: 94
Default

Nominal means "named". A 120/240 volt system has that "name" because of the RMS value.
  #4  
Old 05-28-2009, 10:26 AM
weressl's Avatar
weressl weressl is offline
Senior Member
 
Join Date: Jul 2004
Location: Texas by the Gulf, geat crab, great shrimp
Posts: 3,427
Default

Quote:
Originally Posted by yukonjack_99674 View Post
Can anyone explain to me what is ment by nominal voltage? If you have a 120/240 service, is your nominal voltage the 120 legs to ground? or the 240? I do not understand how you can get 240 to ground. From what Ive read, the circuit is based on the equipment to be used. In other words, if you have 240volt heaters the circuit is considered 240v nominal yet what would be your reference point. You see nominal voltage all over the code book, I must have a thick head. Thanks
Nominal is the system voltage at the distribution point, say 120VAC.
Nominal utilization voltage is the volateg at the user point, that is on the nameplate of the equipment, say 115VAC.

Voltage ranges are the defined highs and lows around the above numbers thata re expoected to be maintained, so the systems and supplies are to be designed to comply with those limitations.

Range A:
Max. Utilization and Service: 126VAC
Min. Service: 114VAC
Min. Utilzation: 110VAC

Range B:
Max. Utilization and Service: 127VAC
Min. Service: 110VAC
Min. Utilzation: 106VAC

So the ranges define the acceptable limits around the nominal.
__________________
Laszlo Z Weress
Staff Engineer

BASF, The Chemical Company

Just because it works it doesn't mean its right!
  #5  
Old 05-28-2009, 03:13 PM
LarryFine's Avatar
LarryFine LarryFine is offline
Senior Member
 
Join Date: May 2005
Location: Richmond, Virginia
Posts: 19,537
Default

Expected, average, normal.
__________________
Code references based on 2005 NEC
Larry B. Fine
Master Electrician
Electrical Contractor
Richmond, VA
  #6  
Old 05-28-2009, 10:28 PM
Pierre C Belarge's Avatar
Pierre C Belarge Pierre C Belarge is offline
Senior Member
 
Join Date: Mar 2006
Location: Westchester County, New York
Posts: 7,753
Default

Quote:
Originally Posted by yukonjack_99674 View Post
Can anyone explain to me what is ment by nominal voltage? If you have a 120/240 service, is your nominal voltage the 120 legs to ground? or the 240? I do not understand how you can get 240 to ground. From what Ive read, the circuit is based on the equipment to be used. In other words, if you have 240volt heaters the circuit is considered 240v nominal yet what would be your reference point. You see nominal voltage all over the code book, I must have a thick head. Thanks

Nominal voltages are like the standard voltages that are produced by the utility company.
Such as 120/240, 120/208, 277/480, 347/600.

Lets say the nominal voltage to the building is 120/240. The Actual Voltage may be 115/235 or something like. The different in actual voltage and Nominal voltage can be caused by many things, such as voltage drop or the transformer tap, etc...The actual voltage can even be higher in value than the nominal voltage.

And then there is voltage to ground. That would be the measurement taken from an ungrounded conductor to the equipment ground.

See Article 100,
Voltage(of a circuit)
Voltage, Nominal
Voltage to Ground

See 220.5(A)Voltages.
__________________
Instructor, Industry Advocate
  #7  
Old 05-28-2009, 10:59 PM
yukonjack_99674 yukonjack_99674 is offline
Junior Member
 
Join Date: Sep 2007
Location: Alaska
Posts: 19
Default thanks

Thank you everyone for the help, I think I have it now. Was'ent that hard after all (once it was explained) thanks
Closed Thread

CEU Banner Forum Pages

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -4. The time now is 06:42 AM.

- Archive - Top

Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.