I am currently working on a project "designing" receptacle placement for a rail yard repair shop. This will have an industrial section to it with welders and crane equipment, but also some offices, break rooms, bathroom/ lockerroom, etc. The reason I am asking this question is that I have been told it is good practice to stagger lighting on different circuits (in your panel) so that if a breakers goes, at least some of the lighting in the area will stay on, as opposed to whole sections of the building going out at a time. This makes perfect sense to me. However, I am being told that it doesn't matter when placing receptacles onto the panel schedule. I was wondering if this same general principle of staggering should be applied when designing receptacle layouts? Should receptacles be staggered so that if a breaker opens, not all of the outlets in the same area go out?
Staggering light circuits is common and in my opinion good practice. I see no reason to extend that to receptacles.
I often do show staggered receptacles, but for a different reason than you are describing. In circumstances for which multi-wire branch circuits are allowed, I will generally go around the room with receptacles powered from, in order, circuit 1, then 3, then 5, then 1, then 3, etc. My intent is to balance the loading and to minimize the magnetic field generated within the conduit. It is not a big deal, however, and certainly not a code requirement.
And due to the requirements for handle ties servicing one leg of that circuit requires shutting off all three legs upsetting approximately 2/3s more people.
I hate that handle tie rule.
Thanks For The Help
Thanks For The Help
Thanks for the help, everyone. Its great hearing everyone's opinions and practices on the matter.
Have a great day,
--Nate
I typically spread the circuits out, too. But it can backfire.
I wired 9 recepts along a church kitchen one time. I wired them 1 3 5 1 3 5 1 3 5. The following week they called and said all three breakers had tripped. [This was before the common - trip requirement]
So I head over and can't find any issues. Next week, same problem. So I drive out again.
Turns out, they didn't want to overload any one circuit so they plugged everything into every third recept. Eventually, all the roasters and coffee makers would trip the breaker, so they just shifted everything to the next receptacles.
So they started out with everything on circuit 1, it would trip, then everything got moved to circuit 3 until it tripped. Then on to 5.
Hilarious! No good deed goes unpunished. Who would think anyone in the kitchen would care to carefully balance the load?