Page 1 of 2 12 LastLast
Results 1 to 10 of 20
Thread: GFCI minimum trip rating
  1. #1
    Join Date
    Feb 2008
    PA
    Posts
    621
    Does anyone know the minimum trip rating for personal protection on a GFCI? Is there a different min. trip rating for equipment protection? Can you get GFCI's with different trip ratings? (I beleive the standard is 6 ma), but can you get one that trips at 9 ma and is still legal?
  2. #2
    Join Date
    Feb 2003
    Florida
    Posts
    7,637
    4-6 mA. See the FPN to GFCI in Article 100 of the NEC.
    Bryan P. Holland, MCP
    NEMA - Codes & Standards
  3. #3
    Join Date
    Jul 2007
    Iowegia
    Posts
    17,806
    4-6ma is the only range acceptable for personnel protection.
  4. #4
    Join Date
    Aug 2008
    Tampa Florida
    Posts
    244
    Quote Originally Posted by SiddMartin View Post
    The equipment ground protection is designed to protect the equipment and not personnel. The ground fault setting depends on the size of the equipment and the circuit to which it is connected. These setting are usually high enough to kill a person.
  5. #5
    Join Date
    Jul 2003
    New Jersey
    Posts
    24,762
    I agree, Class A GFCI's trip between 4-6 ma. Older Class B GFCI's trip at a minimum of 20 ma and are not suitable for personal protection. GFPE protection used for protecting equipment will trip at 30 ma.
    Rob
  6. #6
    Join Date
    Feb 2003
    Wisconsin
    Posts
    9,840
    Quote Originally Posted by infinity View Post
    I believe Class B GFCI's were for old pool lighting fixtures.
    Just because you can, doesn't mean you should.
  7. #7
    Join Date
    Jun 2007
    Warren, MI
    Posts
    923
    It may be 4-6ma but what's the allowable trip time? I don't have a link handy for one of those charts. You may be surprised at the lenght of the allowable trip times!
    Bill
  8. #8
    Join Date
    Jul 2007
    Iowegia
    Posts
    17,806
    Quote Originally Posted by wptski View Post
    According to P&Ss website, the trip time is 0.025 seconds nominal.
  9. #9
    Join Date
    Jul 2003
    New Jersey
    Posts
    24,762
    Quote Originally Posted by jim dungar View Post
    That's correct. Dates back to the 70's I believe.
    Rob
  10. #10
    Join Date
    Jun 2007
    Warren, MI
    Posts
    923
    Quote Originally Posted by 480sparky View Post
    The current and time are like two different things. I can't find one of those current vs time curves but somebody stated 6ma at 7.2 seconds which is what I'm getting at. I tested some P&S and Leviton a while back. The Leviton's trip time was over .1 seconds.
    Bill
Posting Permissions
  • You may not post replies
  • You may not edit your posts