Can this inusualtion be??
Smart $
Esteemed Member
Ohio
Specs says RHH/RHW-2/USE-2 Low smoke zero halogen. Can you have both? Aren't they both insulations?
I see 3... so are referring to any 2 in particular?
That said, it is not uncommon to have insulation which meet the standards for more than one type and labeled as such.
jmellc
Durham, NC
Facility Maintenance Tech. Licensed Electrician
A lot of wire is multi labeled as THWN & THHN, or also MTW as well.
mstrlucky74
NJ
For example can you have a USE-2 wire with LSZH also? These are not BOTH insulation types? I would say not because I have seen this wire before.
Maybe LSZH is the jacket and not the insulation
Joe Villani
Yes. However since you can't use USE-2 in a building it will have another rating also as RHW (for example)
To achieve the LSZH additional additives are added to the insulation.
I have seen this as a spec in tunnels and shafts.
General cable is one manufacturer that has this type of product.
Smart $
Esteemed Member
Ohio
LSZH ( or LSOH or LS0H or LSFH or OHLS) is an additional classification for the jacket/insulation... but it has nothing to do with conductor insulating properties, at least not directly. Somewhat similar to conductor types that are additionally labeled sunlight resistant.