Thread: Gray PVC vs White PVC

  1. #1
    Join Date
    Jul 2007
    Posts
    7

    Gray PVC vs White PVC

    I need help to settle a disagreement. Under the NEC can you use white plumbing PVC in leu of gray listed PVC?

  2. #2
    Join Date
    Nov 2007
    Location
    East of 480sparky
    Posts
    1,121
    i think you already answered your question..

    listed PVC
    page 106 UL White Book 2008

    ........includes the UL symbol together with the word "LISTED", a control number and the product name

  3. #3
    Join Date
    Feb 2003
    Location
    New Jersey
    Posts
    2,406
    Probably, as long as it's buried. Try getting fittings to match though. It's a little tough pulling wire through a plumbing "L":grin:

  4. #4
    Join Date
    Feb 2003
    Location
    Illinois
    Posts
    19,003
    352.6 Listing Requirements.
    PVC conduit, factory elbows, and associated fittings shall be listed.
    Don, Illinois
    "It is the first responsibility of every citizen to question authority." B Franklin

  5. #5
    Join Date
    Mar 2008
    Location
    Las Vegas
    Posts
    264
    This topic was visited a few weeks ago. Since, in the listings, white plumbing PVC is NOT listed as an electrical raceway, it is not suitable for use as one.
    Kevin

    Certified Electrical Inspector/Former E.C.

  6. #6
    Join Date
    Mar 2006
    Location
    Tampa Florida
    Posts
    8,009
    It will work just fine but without the UL not legal.

  7. #7
    Join Date
    Aug 2008
    Location
    NH
    Posts
    1,249
    Quote Originally Posted by Sam Branch View Post
    I need help to settle a disagreement. Under the NEC can you use white plumbing PVC in leu of gray listed PVC?
    I would never pass it :grin:
    "Appliances and wiring will burn out to protect fuses"

  8. #8
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    18,933
    Quote Originally Posted by Sam Branch View Post
    I need help to settle a disagreement. Under the NEC can you use white plumbing PVC in leu of gray listed PVC?

    What are you using for? As a sleeve it's fine as a raceway it isn't.
    Rob

    Chief Moderator

    All responses based on the 2011 NEC unless otherwise noted

  9. #9
    Join Date
    Feb 2009
    Location
    Western KY on the Ohio River
    Posts
    140
    As I recall, water pipe has a pressure rating and electrical conduit has a temperature rating.

  10. #10
    Join Date
    Mar 2006
    Location
    Tampa Florida
    Posts
    8,009
    One problem is by using white you might mis lead a plumber that cuts into it by mistake thinking its water. Best just use gray.

    Did use 2" gray once on a house i was building for a vent pipe. Inspector was not happy but being he knowed me and explained simply that i was out of white and had gray. Legally he could have red tagged but he used logic and passed it.

    Now if i am on a job and need a 3/4 coupling and am out i would borrow one from plumber and hope inspector not make issue.