    EMT Strapping Code

    Does anyone know the exact interpretation of the EMT Min strapping req. The code states EMT must be strapped with in 3' of boxes, panels, conduit bodies, etc. and every 10' there after. Does this mean you must have a strap within 3' of a set screw coupling?

  2. #2
    Join Date
    Jul 2007
    Location
    Iowegia
    Posts
    16,849
    Couplings are not terminations, so you don't need to support within 3'.

  3. #3
    Join Date
    Feb 2003
    Location
    Bremerton, Washington
    Posts
    6,626
    The 2008 NEC adds a requirement for support between two boxes, if 18" or less with no concentrics, support is not needed.
    Moderator-Washington State
    Ancora Imparo

  4. #4
    Join Date
    May 2009
    Location
    Columbus, ga
    Posts
    104
    but spec codes say otherwise, within ten inches of boxes. so there is a difference in spec(blueprint)codes and nec. so you would also need to check the blueprint, even though the nec says 3'

  5. #5
    Join Date
    Jul 2007
    Location
    Iowegia
    Posts
    16,849
    Quote Originally Posted by sparkyboys View Post
    but spec codes say otherwise, within ten inches of boxes. so there is a difference in spec(blueprint)codes and nec. so you would also need to check the blueprint, even though the nec says 3'
    Job specs can say anything. 10", 5", 8", 22.517".....

  6. #6
    This one is confusing for me. I have failed inspections for not strapping EMT within 3' of a coupling. Was the EI wrong on this correction? I know strapping is req. within 3' of boxes and other termination points but is a coupling a "tubular termination"?

  7. #7
    Join Date
    Mar 2006
    Location
    Tampa Florida
    Posts
    8,009
    Quote Originally Posted by Dustin Foelber View Post
    This one is confusing for me. I have failed inspections for not strapping EMT within 3' of a coupling. Was the EI wrong on this correction? I know strapping is req. within 3' of boxes and other termination points but is a coupling a "tubular termination"?
    Your fault for not demanding code number and reading it. Yes inspectors can be wrong. Or you might have a local code.

  8. #8
    Join Date
    Feb 2003
    Location
    Massachusetts
    Posts
    48,632
    Quote Originally Posted by Dustin Foelber View Post
    This one is confusing for me. I have failed inspections for not strapping EMT within 3' of a coupling. Was the EI wrong on this correction?
    What code cycle?

    The NEC used to require within 3 feet of a fitting.

  9. #9
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    19,117
    The EI was wrong unless this was a long time ago. This is from the 1999 NEC:

    Rob

    Chief Moderator

    All responses based on the 2011 NEC unless otherwise noted

  10. #10
    Prior to what year was the 3' within fitting req?