About breakers for pool pumps

Status
Not open for further replies.

jumper

Senior Member
2011 NEC

680.21(C) GFCI Protection. Outlets supplying pool pump motors
connected to single-phase, 120 volt through 240 volt branch
circuits, rated 15 or 20 amperes, whether by receptacle or by
direct connection, shall be provided with ground-fault circuitinterrupter
protection for personnel.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The 2014 NEC requires all single phase pool pumps 120-240V to be gfci protected

(C) GFCI Protection. Outlets supplying pool pump motors
connected to single-phase, 120-volt through 240-volt
branch circuits, whether by receptacle or by direct connection,
shall be provided with ground-fault circuit-interrupter
protection for personnel.
 