    photocell wiring

    We have an old building that is 240 volt. The outside lights are 2pole 240. The photocell that was rated 208/240. This might be a stupid question but the photocell only has three wires. Black, white, and red. How does this work on 240v?

  2. #2
    Join Date
    Jul 2007
    Location
    Iowegia
    Posts
    16,905
    It opens one (ungrounded) wire of the circuit.

  3. #3
    Join Date
    Feb 2003
    Location
    Massachusetts
    Posts
    49,474
    Quote Originally Posted by 480sparky View Post
    It opens one (ungrounded) wire of the circuit.

    I agree with 480sparky but will add if these are HID fixtures you have an issue with 410.54(B)

  4. #4
    Join Date
    Jul 2008
    Location
    Michigan
    Posts
    1,904
    Quote Originally Posted by iwire View Post
    I agree with 480sparky but will add if these are HID fixtures you have an issue with 410.54(B)
    Section 410.54(B) ?

  5. #5
    Join Date
    Feb 2003
    Location
    Massachusetts
    Posts
    49,474
    Quote Originally Posted by SEO View Post
    Section 410.54(B) ?
    Going from memory but if that is the section I am thinking of it requires the 'auxiliary equipment' (AKA the ballast) to have all ungrounded conductors opened.

  6. #6
    Join Date
    Jul 2008
    Location
    Michigan
    Posts
    1,904
    Bob I must be overlooking the code section could you help?

  7. #7
    Join Date
    Apr 2008
    Location
    Austin, TX
    Posts
    1,021
    410.104(B)

    I would think "all conductors" means the grounded one as well.

  8. #8
    Join Date
    Jul 2008
    Location
    Michigan
    Posts
    1,904
    That looks like the code section, the way I read it the ungrounded conductors are switched. I was hoping Bob would reply .

    Thanks jeremy.

  9. #9
    Join Date
    Feb 2003
    Location
    Portage, Indiana NEC: 2008
    Posts
    9,911
    410.54(B) Switching. Where supplied by the ungrounded conductors of a circuit, the switching device of auxiliary equipment shall simultaneously disconnect all conductors.
    I can see this read two ways:

    1. where the switching device is fed by only ungrounded conductors, then the device has to switch all conductors?

    2. where the switching device is fed by a grounded conductor (as in this case) doesn't need to switch all conductors?

    Let the debate begin:grin:
    Wayne A. From: N.W.Indiana
    Be Fair, Be Safe
    Just don't be fairly safe

  10. #10
    Join Date
    Jul 2008
    Location
    Michigan
    Posts
    1,904
    hurk27 I think you mean 410.104 (B).