    I have been told that there is some code against making up your own extension cords on the job. does anyone have any reason that you couldnt make up a cord out of say 12-3 so cord and some male and female listed cord caps??
    The tail does NOT wag the dog.
  2. #2
    Join Date
    Jan 2008
    NC & IN
    Posts
    3,313
    What box are you going to use ?
  3. #3
    Join Date
    Apr 2004
    Back in Alaska, on a "Jack Bauer" job!
    Posts
    1,708
    Believe it or not, there is a male end, and a female end on a piece of SO cord by the way it lays naturally. If you make up cords by the bunch, you will notice that the Hot, Nuetral, and Ground have a natural fit one way, but extremely difficult the other way? Flip the ends, and it will be a piece of cake.
    Don't let fear be your guide!
  4. #4
    Join Date
    Jul 2003
    New Jersey
    Posts
    24,379
    I thought that it has something to do with an OSHA requirement for cords to have molded ends. I could be wrong. There was a time when all of the cords on the job site were made by the electricians.
    Rob
  5. #5
    Join Date
    Apr 2009
    danbury ct/work in white plains ny
    Posts
    208
    Quote Originally Posted by infinity View Post
    AND no flat cords were allowed (not sure anymore)
    Its
    Been
    Exciting
    Work
  6. #6
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    This may be to old.
    OSHA Standard Interpretations 03/03/1992 - Contractor shop-made extension cords
    In regard to electrical contractors assembling cord sets at construction sites, the practice is acceptable, provided the assembled cord sets are constructed in a manner equivalent to those that are factory-assembled and approved. (The same approach applies to the General Industry Electrical Standards. However, your question pertained to construction, so the remaining references are to Subpart K of Part 1926.) Criteria for determining whether shop-made cord sets meet existing electrical standards include:
    1)All components must be approved for the purpose by a nationally recognized testing laboratory (1926.403(a)). Individual components must be compatible for use with the other components of the completed assembly.
    2)The cord set must meet all applicable requirements of Subpart K. For example, the assembly must be marked appropriately (1926.403(g)); boxes intended for use in a permanent installation may not be used (1926.403(b)(1)(i)); cords must be connected to devices and fittings so as to provide strain relief (1926.405(g)(2)(iv)); cords passing through holes in enclosures must be protected by bushings or fittings designed for the purpose (1926.405(g)(2)(v) fittings designed to fasten cables to metal boxes are not acceptable); and no grounded conductor shall be attached to any terminal or lead so as to reverse designated polarity (1926.404(a)(2)).
    3)The cord set must be assembled by a qualified person.
    4)The wiring of the completed assembly must be checked before the cord set is first used. For example, the following, or equivalent, tests should be performed:
    (a) All equipment grounding conductors shall be tested for continuity and shall be electrically continuous.
    (b) Each receptacle and attachment plug shall be tested for correct attachment of the equipment grounding conductor. The equipment grounding conductor shall be connected to its proper terminal.
  7. #7
    Join Date
    Feb 2003
    Massachusetts
    Posts
    60,020
    Thumbs up
    Quote Originally Posted by Rockyd View Post
    I believe it, once you remember that it becomes much easier to terminate.
    Even when your just putting a cord on equipment it is worth checking to see if you have the right end of the cord that lines up with the male plug. :smile:
  8. #8
    Join Date
    Mar 2008
    Oklahoma
    Posts
    1,737
    Quote Originally Posted by quogueelectric View Post
    Im thinking because the completed cord would not be a UL listed assembly is the reason. Even though the individual components where. Im glad I dont live where inpectors enforce this level of nonsense.
    "Mule"
    Yes, Im stubborn as a mule..that's why,
    I'm a "Has Been" that "Never Was"
    :D
  9. #9
    Join Date
    Mar 2006
    Westchester County, New York
    Posts
    8,221
    It is permitted to make up extension cords for the construction site(s). It is also permitted to make limited repairs to extension cords as well.
    As you can see in Bob's post, there are guidelines that OSHA has you to follow. It is not hard to do, as long as you are using listed parts and the proper cords.
    There may be local restrictions, that would be my only guess as to why some say it is not permitted.
    Instructor, Industry Advocate
  10. #10
    Join Date
    Dec 2006
    Eastern Oregon
    Posts
    3,451
    I never noticed! I'm gonna have to start looking for it now when I make up cord ends!