Preferred cable type

Status
Not open for further replies.
I've installed various types of 5 Kv equipment using the okonite yellow armored cable running in cable trays. I have a scenario that there isn't enough room for a tray and want to use RGS conduit within an electrical room to install a tie breaker between two existing 2400V, 1200A switchgear. What is the best cable to use?
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
If the rated current of installation is 1200 A [see NEC 215.2 Minimum Rating and Size. B) Feeders over 600 Volts] then two groups of three cables- each group in separate conduit-of 1000 MCM copper- in conditions as per Table 310.60(C)(73) - will be good. A clearance of at least one conduit diameter shall be kept between conduits.
 
Thank You Sir!

Thank You Sir!

If the rated current of installation is 1200 A [see NEC 215.2 Minimum Rating and Size. B) Feeders over 600 Volts] then two groups of three cables- each group in separate conduit-of 1000 MCM copper- in conditions as per Table 310.60(C)(73) - will be good. A clearance of at least one conduit diameter shall be kept between conduits.

Thanks for the help!
 