How do i have to do coduit fill for a wire thats not in the table 5 of chapter 9.
The wire is 4/0 USE-2. There is no such wire in the table 5.
USE-2 is not a wire, it is a cable - Chap. 9, Note 9 describes how to determine the area of a cable.
RE: "Conductors marked only USE * are not allowed to be brought inside a building..."
I know I'm going to get an argument, however, there is nothing in the code that says you cannot bring USE into a building...the code says USE shall not be used for interior wiring.
UL 2008 White Book - Service Cable [TXKT] ..."USE & USE-2 are not suitable for use in premises or aboveground
except to terminate at the service equipment..."
As a building inspector I believe I would allow someone to install 2-1/2 ft. of USE-2 inside a raceway terminating in service equipment inside a structure; if anyone were to question me I would show them the UL White Book and let them argue until they were blue in the face...bottom line, the permit card gets signed.