M. D.

Senior Member
I would take Hardworking"s approach isolate each item and see,.. My thought is the photo/ contactor is the cause ..
 

iwire

Moderator
Staff member
Location
Massachusetts
Lou, a GFCI device on the primary side of a transformer will not 'see' a ground fault on the secondary side of the transformer. A ground faulted secondary will only cause a larger line to line current on the primary side.


Assuming a grounded system on the secondary side a ground fault on the secondary will just loop back to the grounded phase / neutral of the transformer.
 

hardworkingstiff

Senior Member
Location
Wilmington, NC
Lou, a GFCI device on the primary side of a transformer will not 'see' a ground fault on the secondary side of the transformer. A ground faulted secondary will only cause a larger line to line current on the primary side.


Assuming a grounded system on the secondary side a ground fault on the secondary will just loop back to the grounded phase / neutral of the transformer.

Thanks Bob, I thought as much but wasn't sure.

So the OP's problem is on the primary side.
 