    Load Calculation - Wire Size

    On the attached load calculation, does the feeder ampacity have to be large enough to carry the Calc kva, or the balanced 3 ph amps ?

    which value do I use :-?
    Attached Files Attached Files

  2. #2
    Join Date
    Jun 2006
    Location
    Ohio
    Posts
    12,939
    Quote Originally Posted by texassparky View Post
    On the attached load calculation, does the feeder ampacity have to be large enough to carry the Calc kva, or the balanced 3 ph amps ?

    which value do I use :-?
    Same difference.

    2650kVA/480V/1.732=3190A (rounded to 3 sig' fig's)

  3. #3
    Join Date
    Jul 2009
    Location
    Dallas / Ft. Worth
    Posts
    95
    Ahhh...kva to amps thanks !