Results 1 to 3 of 3
Thread: Load Calculation - Wire Size
  1. #1
    Join Date
    Jul 2009
    Dallas / Ft. Worth
    Posts
    95
    On the attached load calculation, does the feeder ampacity have to be large enough to carry the Calc kva, or the balanced 3 ph amps ?
    which value do I use :-?
  2. #2
    Join Date
    Jun 2006
    Ohio
    Posts
    21,077
    Quote Originally Posted by texassparky View Post
    Same difference.
    2650kVA/480V/1.732=3190A (rounded to 3 sig' fig's)
  3. #3
    Join Date
    Jul 2009
    Dallas / Ft. Worth
    Posts
    95
    Ahhh...kva to amps thanks !
Posting Permissions