yukonjack_99674
Member
- Location
- Alaska
I have 103v on the neutral of a 120v circuit is. The voltage goes away when I wire nut several other neutrals together, (pig tails to other outlets of the same circuit). The transformer is 208v and the neutral is being shared with the 3 phases which form the 3 circuits. I have checked the Xo at the transformer, it is landed correctly. I checked the integrity of the 208v phasing to make sure that two legs were not on the same phase, all seems ok there also. I have not checked (yet) to see if a different neutral has been introduced into the circuit, as that little task will be intense. Any ideas? what did I miss? Thanks