    aluminum wiring

    Hey guys went on a service job tonight doing an al/cpr device changeout. The original electricians cut off the grounds maybe 3 inches in the boxes. What is the proper way of bonding these plugs? Wagos? Screw on the clamps in the box? WIth a copper wire on a ground screw coming off the box? Wirenuts not an option not enough wires. How would you fix it?

  2. #2
    Join Date
    Sep 2004
    Location
    Ohio
    Posts
    704
    I would ground the box with that short wire and use self-grounding receptacles.
    gusco

  3. #3
    Join Date
    Feb 2003
    Location
    Minnesota
    Posts
    5,006
    Quote Originally Posted by guschash View Post
    I would ground the box with that short wire and use self-grounding receptacles.
    I'll bet the boxes are non-metallic.

    Short aluminum EGCs. . . yeesh. And the boxes are probably already "hammer handle tight". AlCop, Copalum, or Purple Ideals, or someother type of listed Al/Cu pressure connector needs to be used.
    Another Al in Minnesota

  4. #4
    Join Date
    Dec 2008
    Location
    Raleigh NC
    Posts
    268
    Alumiconns.....

    http://www.alcopstore.com/index.asp?...ATS&Category=2

    With that small of a wire, they will still be a pain to install, but definitely do-able.

    Why is it that all houses wired in aluminum seem to have short pigtails? I just completely re-wired a house that was aluminum, and it had the most consistently short pigtails of any house I'd ever seen.

  5. #5
    Join Date
    Feb 2003
    Location
    Minnesota
    Posts
    5,006
    Quote Originally Posted by MarkyMarkNC View Post
    Why is it that all houses wired in aluminum seem to have short pigtails?
    I well remember wiring a couple houses, when I was apprenticing back in the late 60's, where my Master didn't give a rip about box volume calcs, and approached the whole matter as if the box was sized based upon the size of the breaker.

    That is, one used the same size boxes for the same roping that one would with copper wire.

    Boy we had to keep the leads short to get 'em in under the devices. . . .
    Another Al in Minnesota

  6. #6
    Join Date
    Nov 2008
    Location
    gulf coast
    Posts
    250
    Al did they break off just as easily back then or is that due to heating and expanding? Had to change the panel today. Biggest pita ive ever had. Ended up splitbolting the 10 wires cause they were stranded and would not fit under square d qos pressure lugs. Learned so much today. Thank God for modern concepts.

  7. #7
    Join Date
    Feb 2003
    Location
    Minnesota
    Posts
    5,006
    Quote Originally Posted by billdozier View Post
    Al did they break off just as easily back then or is that due to heating and expanding?
    That early alloy was supple, but nicks would migrate through the conductor. Most stripping methods commonly accepted left nicks. . . bad juju.

    The thermal expansion of the aluminum under plain old device terminal screws deformed the conductor leading to higher terminal resistance, greater heating and more deformation. . . vicious cycle.
    Another Al in Minnesota