NEC 310.60 (C) (2)(b) permitted cable derating

Status
Not open for further replies.

wgmacfarlane

New member
Why does the NEC article 310.60(c)(2)(b) say where the burial depths are deeper than shown in a specific underground ampacity table or figure, an ampacity derating of 6% per ft increase in depth for all values of rho shall be "permitted".
Should it not say required?
The consequenses are a reduction of cable life.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Good question. You have seven more days to submit a suggested revision to the NFPA (for the 2017 edition).

My only guess is based on the fact that the entire article addresses the determination of ampacity under engineering supervision. I think they are simply giving us a process that has their blessing, without actually telling us how to do our jobs.

Welcome to the forum.
 