680.26 equipotential bonding conductor burial requirements

Status
Not open for further replies.

erickench

Senior Member
Location
Brooklyn, NY
Greg, IMHO the equipotential bonding grid would not need to meet the burial depth requirements of 300.5 unless specifically referenced in 680.26. Article 300 is titled "wiring methods", the bonding conductors of the equipotential bonding grid would not be a "wiring method" IMHO.

Chris

I agree with raider1. There are sections in article 680 that reference chapter 3 wiring methods but only in certain cases. In the case of pools it would apply to wiring run from the interior of a one family dwelling to a pool motor.:wink:
 