Can E.G.C be ran separate of parallel M.C conductors?

Status
Not open for further replies.
Hello everyone this is my first post. I must have incorrectly submitted my first entry so I'll try to be more concise. I have been red tagged for the size of my E.G.C in a set of paralleled M.C cable. Inspector is stating I must have a #1 Al E.G.C instead of the #2 as per 250.122. He is correct (know this now, have never been cited for this before). So Im trying to rectify this in the fast and least expensive way. So the questions is can I run a seperate M.C cable and use two of the conductors as my E.G.C for the current carrying conductors I ran in parallel?They would all be of equal size. Is there a code reference that prohibits this? Thank you in advance for replying.
 