Thread: Myers Hub for Outdoor Panel

  1. #1

    Myers Hub for Outdoor Panel

    Do I have to install Myers Hubs at service panel for feeder cks? It's an outdoor panel, and I thought compression connectors with silicone would work.

  2. #2
    Join Date
    Jun 2005
    Location
    North Logan, Utah
    Posts
    7,939
    Where will the feeder conduit enter the service?

    Take a look at 312.2

    I thought compression connectors with silicone would work.
    I would not use rain tight compressions connectors with just silicone. Use a sealing lock ring to connect the RT compression connector.

    Chris

  3. #3
    Join Date
    Apr 2005
    Location
    Atlanta,GA
    Posts
    3,989
    Quote Originally Posted by euclid43 View Post
    Do I have to install Myers Hubs at service panel for feeder cks? It's an outdoor panel, and I thought compression connectors with silicone would work.
    You here this all the time. Would this work? It may very well work but is it an approved method.

    approved: acceptable to the authority having jurisdiction.
    "A sight for sore eyes to the blind would be awful magestic"---Wax Fang

  4. #4
    Join Date
    Feb 2007
    Location
    USA
    Posts
    3,879
    I think the question asked is if a Raintight connector with a Sealing washer/ring is code complaint to install a raceway entering in th top of a panel
    Or do you need to use a myers type hub?

  5. #5
    Join Date
    Apr 2005
    Location
    Atlanta,GA
    Posts
    3,989
    Quote Originally Posted by euclid43 View Post
    I thought compression connectors with silicone would work.
    Quote Originally Posted by Sierrasparky View Post
    I think the question asked is if a Raintight connector with a Sealing washer/ring is code complaint to install a raceway entering in th top of a panel
    Or do you need to use a myers type hub?
    I would think that the newer compression connectors with sealing washers would be code compliant, they are listed for "wet" locations.

    However not all compression connectors are raintight. Even some of the one's that people thought were raintight.

    If you have one of the new rain tight connectors then you wouldn't need silicone. It will be marked "raintight" and have the washer/sealing ring/ thingy.
    "A sight for sore eyes to the blind would be awful magestic"---Wax Fang

  6. #6
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    19,256
    Where is the conduit entering? If it's below the live parts a standard locknut/connector would be complaint.
    Rob

    Chief Moderator

    All responses based on the 2011 NEC unless otherwise noted

  7. #7
    Join Date
    Jun 2005
    Location
    North Logan, Utah
    Posts
    7,939
    Quote Originally Posted by infinity View Post
    Where is the conduit entering? If it's below the live parts a standard locknut/connector would be complaint.
    I agree, thats why I mentioned that the OPer should read 312.2.

    Chris

  8. #8
    Join Date
    May 2007
    Location
    Fort Lauderdale/ Miami
    Posts
    1,639
    Sealing locknuts are only good for threaded conduit, not fittings.
    Myers hubs are cheap and work just fine. If you are entering below the panel guts, just a regular compression connector rated for outdoor use will work.

  9. #9
    Join Date
    Apr 2003
    Location
    Planet macmikeman
    Posts
    3,037
    Quote Originally Posted by jrannis View Post
    Sealing locknuts are only good for threaded conduit, not fittings.
    Myers hubs are cheap and work just fine. If you are entering below the panel guts, just a regular compression connector rated for outdoor use will work.
    At the UL website there is a question and answer section that covers different listing issues. One article was about the use of Myers hubs and emt. The UL position was that emt in a Myers hub is against the listing. The reference is UL Question Corner, May 14, 2006.
    85deg. an Sunny today.

  10. #10
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    19,244
    Quote Originally Posted by macmikeman View Post
    At the UL website there is a question and answer section that covers different listing issues. One article was about the use of Myers hubs and emt. The UL position was that emt in a Myers hub is against the listing. The reference is UL Question Corner, May 14, 2006.
    I used to use myers hubs with emt fittings, then they came up with the fittings that are supposed to be raintight with the rubber washer included.

    I stopped using the myers hubs because the rubber washer should seal the opening in the enclosure.

    recently went back to a job done one year ago to do some additional work and saw that many of the rubber washers were deteriorated enough that I questioned wether they were sealing the opening anymore. Now I plan to use myers hubs again and don't care if they are not listed. The testing labs can not tell me that the original install did not seal.

    When they first came out with the "raintight" fittings I thought they were a joke. Sure the extra nylon ferrules in the fitting probably will keep out more water. But I don't believe are necessary unless you are talking about high pressure water maybe.

    A metal raceway installed outdoors gets more water inside from condensation then it will ever get from rain. I may even be willing to bet that a set screw fitting (if it is a pretty tight fitting one) will hold out more rain than what condenses within the raceway.