Thread: mc cable with aluminum ground

  1. #1
    Join Date
    Apr 2009
    Location
    Olathe, Kansas 338 mi SE of Wingedhorses
    Posts
    1,967

    mc cable with aluminum ground

    There has been much dissucission at our shop about the proper termination of the ground wire. Some say cut off the aluminum ground before it enters the connector and the cable jacket is your ground path. Others suggest that you terminate the aluminum ground inside the box but we do not have copper to aluminum wire nuts to attach to the boxes pig tail.

  2. #2
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    19,404
    Cut it off. Its' only function is to have intimate contact with the metal jacket. Terminating it is not required. Here's an illustrated version:

    http://www.southwire.com/documents/MCAP_BrochureNEW.pdf
    Rob

    Chief Moderator

    All responses based on the 2011 NEC unless otherwise noted

  3. #3
    Join Date
    Jul 2004
    Location
    Louisville, Kentucky
    Posts
    1,947
    Quote Originally Posted by infinity View Post
    Cut it off. Its' only function is to have intimate contact with the metal jacket. Terminating it is not required. Here's an illustrated version:

    http://www.southwire.com/documents/MCAP_BrochureNEW.pdf
    At step two instead of cutting, I make a few wraps around the outside of the cable.
    Norb
    My Boss is a Tyrant and my Employee is an Idiot.

  4. #4
    Join Date
    May 2009
    Posts
    9
    Does any one know if this is available in stranded?

  5. #5
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    12,850
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  6. #6
    Join Date
    Mar 2003
    Location
    New England
    Posts
    10,430
    The OP could also be talking about AC cable and confusing the bonding wire with an EGC.

  7. #7
    Join Date
    Aug 2007
    Location
    Stratford, CT
    Posts
    402
    Quote Originally Posted by 1793 View Post
    At step two instead of cutting, I make a few wraps around the outside of the cable.
    I hope you are only talking about AC cable and not the MCI-A (MCap) type cable. In wrapping this larger aluminum conductor around the sheath, you could inadvertently cause damage to the sheath when the connector clamp is tightened down, or if using a snap-in product, you will cause the fitting not to meet the mechanical or electrical specifications.

    In the case of the MCI-A cable, follow the manufacturer's instructions.
    Larry

  8. #8
    Join Date
    Jul 2004
    Location
    Louisville, Kentucky
    Posts
    1,947
    Quote Originally Posted by LJSMITH1 View Post
    I hope you are only talking about AC cable and not the MCI-A (MCap) type cable. In wrapping this larger aluminum conductor around the sheath, you could inadvertently cause damage to the sheath when the connector clamp is tightened down, or if using a snap-in product, you will cause the fitting not to meet the mechanical or electrical specifications.

    In the case of the MCI-A cable, follow the manufacturer's instructions.

    I have not as of late run any MCI-A (MCap). I run into this with the older armor cables, BX. What I wrap is a very thin, flat something - I would not even call it a "wire".
    Norb
    My Boss is a Tyrant and my Employee is an Idiot.

  9. #9
    Join Date
    Aug 2007
    Location
    Stratford, CT
    Posts
    402
    *whew*...I thought you were talking about type MC.

    BX is now referred to as Type AC, and has the thin bond conductor. Wrapping that on the outside won't have any impact to the fitting or performance.
    Larry

  10. #10
    Join Date
    Jul 2004
    Location
    Louisville, Kentucky
    Posts
    1,947
    Quote Originally Posted by LJSMITH1 View Post
    *whew*...I thought you were talking about type MC.

    BX is now referred to as Type AC, and has the thin bond conductor. Wrapping that on the outside won't have any impact to the fitting or performance.
    Now that would be a task in itself. I have been known to do some wild things but that is not one of them.:grin:

    Old habits and or terms are hard to break.
    Last edited by 1793; 09-24-09 at 12:54 PM. Reason: add final remark