Do you think 550.32(C) would allow a mobile home with a 100A service to have two 50A receptacles used to feed the inside panel. The 100A service is a 100A MB panel. Each receptacle is protected by a 50A breaker in the service panel. There are two cords, each with a 50A plug/cord cap, the other end is hardwired into the inside panel. The inside panel is a split bus panel. It has two 50A main breakers and each cord lands on a 50A breaker. Each main breaker protects one bus section.
This is an existing installation that I had to replace the service due to the ice storm we had.
I didn't take the time to check out all the requirements at the time. I just wanted to get the peoples power back on because of the freezing temperatures. The HO sent me a picture of the "rejection" sticker left by the inspector. I haven't talked to him yet, but I'm sure the cords, plugs, and receptacles are what he rejected it on.
This is an existing installation that I had to replace the service due to the ice storm we had.
I didn't take the time to check out all the requirements at the time. I just wanted to get the peoples power back on because of the freezing temperatures. The HO sent me a picture of the "rejection" sticker left by the inspector. I haven't talked to him yet, but I'm sure the cords, plugs, and receptacles are what he rejected it on.
550.32(C)
(C) Rating. Mobile home service equipment shall be rated
at not less than 100 amperes at 120/240 volts, and provisions
shall be made for connecting a mobile home feeder
assembly by a permanent wiring method. Power outlets
used as mobile home service equipment shall also be permitted to contain receptacles rated up to 50 amperes
with appropriate overcurrent protection. Fifty-ampere receptacles
shall conform to the configuration shown in
Figure 550.10(C).