    Megger data

    Would someone be knid enough to share with me their form for recording the information obtained during a megger test. Our megger is not fancy enough to print out a report so I'm stuck with the old fasion way.

    As I recall the form usually has you note the temperature and relative humidity as well as all of your different readings.

    Thanks for your help.

  2. #2
    Join Date
    Feb 2005
    Location
    Charlotte, NC
    Posts
    6,367
    Quote Originally Posted by shockin View Post
    Would someone be knid enough to share with me their form for recording the information obtained during a megger test. Our megger is not fancy enough to print out a report so I'm stuck with the old fasion way.

    As I recall the form usually has you note the temperature and relative humidity as well as all of your different readings.

    Thanks for your help.
    Testing what?

  3. #3
    Join Date
    Mar 2006
    Posts
    342
    Sorry - should have been more specific.

    We will just be testing service entrance conductors (6 sets of 750 CU) as well as some feeder conductors.

    I believe we will probably meg the switcchboard as well. (After disconnecting the electronics from the main breaker)

    Thanks

  4. #4
    Join Date
    Feb 2005
    Location
    Charlotte, NC
    Posts
    6,367
    Quote Originally Posted by shockin View Post
    Sorry - should have been more specific.

    We will just be testing service entrance conductors (6 sets of 750 CU) as well as some feeder conductors.
    Mine are in Excel format, this forum won't allow me to attach those, I assume these are low voltage cables, you can email me or download test forms at www.megger.com

    Quote Originally Posted by shockin View Post
    I believe we will probably meg the switcchboard as well. (After disconnecting the electronics from the main breaker)
    And the PT's, and the lightning arrestors, lots to consider depending on the equipment. Are you testing the breakers as well?

  5. #5
    Join Date
    Mar 2006
    Posts
    342
    The cables are low votage (480v)

    I do not intend to test the breakers. Do you generally test the breakers on a new installation?

  6. #6
    Join Date
    Feb 2005
    Location
    Charlotte, NC
    Posts
    6,367
    Quote Originally Posted by shockin View Post
    Do you generally test the breakers on a new installation?
    Yes, always. And the transformer, and the relays, and the GFP, etc.... Thats all I have done for 20 years. Usually the EC does nothing, a testing comapny comes in after the fact.

  7. #7
    Join Date
    Mar 2006
    Location
    Westchester County, New York
    Posts
    8,169
    Quote Originally Posted by zog View Post
    Yes, always. And the transformer, and the relays, and the GFP, etc.... Thats all I have done for 20 years. Usually the EC does nothing, a testing comapny comes in after the fact.
    Except, you are not using a megger for all of those tests, are you?
    Instructor, Industry Advocate

  8. #8
    Join Date
    Sep 2008
    Location
    Hawaii
    Posts
    91
    Quote Originally Posted by Pierre C Belarge View Post
    Except, you are not using a megger for all of those tests, are you?
    Technically you could because Megger makes all of the different test equipment. But yes, you test the insulation resistance on transformers breakers.

  9. #9
    Join Date
    Feb 2005
    Location
    Charlotte, NC
    Posts
    6,367
    Quote Originally Posted by zog View Post
    Yes, always. And the transformer, and the relays, and the GFP, etc.... Thats all I have done for 20 years. Usually the EC does nothing, a testing comapny comes in after the fact.
    An Insulation resistance test is one of about 5-10 tests done on a breaker and one of 5-20 test done on a transformer.

  10. #10
    Join Date
    Mar 2006
    Location
    Westchester County, New York
    Posts
    8,169
    Quote Originally Posted by zog View Post
    An Insulation resistance test is one of about 5-10 tests done on a breaker and one of 5-20 test done on a transformer.

    Zog
    Do you need a slick motorcycle to properly make such tests?