210.12 AFCI & 210.8 GFCI
JDB3
AFCI protection is required in the kitchen. Verifying that this means the refrigerator? If so, then are you'll using a breaker to do this, since it needs to be readily accessible?
GFCI protection is required for receptacles installed to serve the countertop surfaces.
IF you install an AFCI receptacle for the refrigerator, so that it is readily accessible, then this will probably be in the countertop area, Then it would also need to provide GFCI protection :?
Dennis Alwon
Chapel Hill, NC
Retired Electrical Contractor
Yes
Correct and if the refrigerator is within 6' of the sink it will also need gfci. Dishwasher also needs afci and gfci protection
This is all new to the 2014
Dennis Alwon
Chapel Hill, NC
Yes
John120/240
Olathe, Kansas
For plug mold applications I would install a GFCI in the pantry. Why couldn't you do the same with a AFCI device ?