Article 230.79 & Article 230.42(B)

Status
Not open for further replies.

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I know we been thru this but this is a bit different. IMO, 230.79 talks about minimum rating of the disconnect and 230.42(B) states the conductors must match the amp. of these req. disconnects. I know we all don't agree...

So, we cn agree that 230.79(C) states we need a minimum of a 100 amp disconnect for a one family dwelling however since a multi family dwelling is not listed it appears to fall under (D) All Others which only requires a 60 amp disconnect. Do we agree?

I find it odd and I realize it would be unlikely to have a multi unit dwelling with just a 60 amp service but it looks like the NEC would allow it. YES?
 
Last edited:

retire09

Senior Member
An apartment is still considered to be a one family dwelling.
But an apartment is supplied by a feeder not a service.
Is that your point?
 

retire09

Senior Member
The building is not the same but the individual apartments are the same as a single family dwelling.
A dwelling is the same whether it is a separate house or an apartment.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The building is not the same but the individual apartments are the same as a single family dwelling.
A dwelling is the same whether it is a separate house or an apartment.


I understand but the NEC makes a distinction throughout the NEC but it does not include multifamily in 230.79. It specifically says single family. The building could be fed with a 60 amp service IMO.
 

retire09

Senior Member
A SF dwelling is one dwelling unit in one building.
Multi- family building is 3 or more dwelling units in one building.
See definitions, 220.84 and 215.2
 

david

Senior Member
Location
Pennsylvania
I know we been thru this but this is a bit different. IMO, 230.79 talks about minimum rating of the disconnect and 230.42(B) states the conductors must match the amp. of these req. disconnects. I know we all don't agree...

So, we cn agree that 230.79(C) states we need a minimum of a 100 amp disconnect for a one family dwelling however since a multi family dwelling is not listed it appears to fall under (D) All Others which only requires a 60 amp disconnect. Do we agree?

I find it odd and I realize it would be unlikely to have a multi unit dwelling with just a 60 amp service but it looks like the NEC would allow it. YES?

I agree that a multi family dwelling does not need a min of 100 amp service in conjunction with 220.84 table 220.84

I would think a single family dwelling would not have the load diversity as two family and multifamily dwelling
 

RB1

Senior Member
Dennis,

A 60 amp service is OK for an individual dwelling within a multi-family building provided that the standard calculation method is used. The load diversity for a dwelling unit should be similar (electric heat notwithstanding) regardless of whether it is part a of a multi-family occupancy, or a one- and two-family dwelling.
 