Question 480V Single Phase with Grounded Leg

I am looking for a way create a 480V single phase feeder with one leg grounded. The load is 48KVA. I am trying to create this from a 480/277V, three phase feeder. Does anyone make a 50KVA, 480V-480V single phase transformer ?

Thanks in advance!
__________________
Jeff
"Watt's Up !!"
  #2  
Old 11-17-2009, 03:44 PM
bob's Avatar
bob bob is offline
Senior Member
 
Join Date: Feb 2003
Location: Nashville
Posts: 2,054
Default

Quote:
Originally Posted by jbt260 View Post
I am looking for a way create a 480V single phase feeder with one leg grounded. The load is 48KVA. I am trying to create this from a 480/277V, three phase feeder. Does anyone make a 50KVA, 480V-480V single phase transformer ?

Thanks in advance!
Why do you have to have one leg grounded? Take 2 of the 3 phases plus an egc and you have 480 volts single phase.
  #3  
Old 11-17-2009, 05:00 PM
jbt260 jbt260 is offline
Member
 
Join Date: Mar 2004
Location: Ohio
Posts: 70
Default

Sorry for lack of info. I have to re-feed an existing roadway lighting circuit that is 480V single phase with a grounded leg. The leg is grounded at every light pole.
__________________
Jeff
"Watt's Up !!"
  #4  
Old 11-17-2009, 07:55 PM
bob's Avatar
bob bob is offline
Senior Member
 
Join Date: Feb 2003
Location: Nashville
Posts: 2,054
Default

Quote:
Originally Posted by jbt260 View Post
Sorry for lack of info. I have to re-feed an existing roadway lighting circuit that is 480V single phase with a grounded leg. The leg is grounded at every light pole.
I am not sure that meets the NEC groounding requirements. I believe you need a EGC to each pole rather that using the neutral. Maybe someone will confirm this.
  #5  
Old 11-17-2009, 08:34 PM
Cavie's Avatar
Cavie Cavie is offline
Senior Member
 
Join Date: Mar 2006
Location: SW Florida
Posts: 1,827
Default

480 2 wire single phase. 1 hot 1 neutral and a ground. Very common in street lighting. Something I learned after being an electrican for 40 years.
__________________
Unlimited Electric Contractor/Standard Electric Inspector/Traffic Signal Inspector/Highway Lighting and Level One Traffic Signal Installer.

I know you believe that you understand what you think I said but I'm sure you realize that what you heard is not what I meant.
  #6  
Old 11-17-2009, 08:37 PM
Cavie's Avatar
Cavie Cavie is offline
Senior Member
 
Join Date: Mar 2006
Location: SW Florida
Posts: 1,827
Default

Quote:
Originally Posted by jbt260 View Post
Sorry for lack of info. I have to re-feed an existing roadway lighting circuit that is 480V single phase with a grounded leg. The leg is grounded at every light pole.
Check with your local POCO. Why arn't they supplying you?
__________________
Unlimited Electric Contractor/Standard Electric Inspector/Traffic Signal Inspector/Highway Lighting and Level One Traffic Signal Installer.

I know you believe that you understand what you think I said but I'm sure you realize that what you heard is not what I meant.
  #7  
Old 11-17-2009, 08:47 PM
brian john brian john is offline
Senior Member
 
Join Date: May 2003
Posts: 6,018
Default

Quote:
Originally Posted by Cavie View Post
480 2 wire single phase. 1 hot 1 neutral and a ground. Very common in street lighting. Something I learned after being an electrican for 40 years.
480 VAC Single phase is one hot, one grounded conductor and one EGC. I would think?
  #8  
Old 11-17-2009, 08:54 PM
Johnmcca's Avatar
Johnmcca Johnmcca is offline
Senior Member
 
Join Date: Jan 2006
Location: Mid-Hudson Valley, NY
Posts: 176
Default

Brian,
One hot, one grounded, and one EGC on a 480 systm would yeild 277 volt, unless I'm mistaken.
__________________
John

“For those of us who believe in physics, this separation between past, present and future is only an illusion, however tenacious”- Albert Einstein
  #9  
Old 11-17-2009, 09:20 PM
Cavie's Avatar
Cavie Cavie is offline
Senior Member
 
Join Date: Mar 2006
Location: SW Florida
Posts: 1,827
Default

Quote:
Originally Posted by Johnmcca View Post
Brian,
One hot, one grounded, and one EGC on a 480 systm would yeild 277 volt, unless I'm mistaken.
It is 480 1 leg to ground.
__________________
Unlimited Electric Contractor/Standard Electric Inspector/Traffic Signal Inspector/Highway Lighting and Level One Traffic Signal Installer.

I know you believe that you understand what you think I said but I'm sure you realize that what you heard is not what I meant.
  #10  
Old 11-17-2009, 09:26 PM
jim dungar jim dungar is offline
Moderator
 
Join Date: Feb 2003
Location: Wisconsin
Posts: 5,459
Default

Quote:
Originally Posted by Johnmcca View Post
Brian,
One hot, one grounded, and one EGC on a 480 systm would yeild 277 volt, unless I'm mistaken.
Only if you are starting from a 480Y/277V system.

A single phase 480:480 transformer, like the OP asked about, could be used to create a 480 2-wire secondary which could then be treated the same as any other 2-wire system.
__________________
I think I have already told you more than I know.
Closed Thread

taking exam?  Forums

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump


All times are GMT -4. The time now is 06:43 AM.

- Archive - Top

Powered by vBulletin® Version 3.7.3
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.