I am looking for a way create a 480V single phase feeder with one leg grounded. The load is 48KVA. I am trying to create this from a 480/277V, three phase feeder. Does anyone make a 50KVA, 480V-480V single phase transformer ?
Thanks in advance!
__________________
Jeff "Watt's Up !!" |
|
#2
|
||||
|
||||
|
Why do you have to have one leg grounded? Take 2 of the 3 phases plus an egc and you have 480 volts single phase.
|
|
#3
|
|||
|
|||
|
Sorry for lack of info. I have to re-feed an existing roadway lighting circuit that is 480V single phase with a grounded leg. The leg is grounded at every light pole.
__________________
Jeff "Watt's Up !!" |
|
#4
|
||||
|
||||
|
I am not sure that meets the NEC groounding requirements. I believe you need a EGC to each pole rather that using the neutral. Maybe someone will confirm this.
|
|
#5
|
||||
|
||||
|
480 2 wire single phase. 1 hot 1 neutral and a ground. Very common in street lighting. Something I learned after being an electrican for 40 years.
__________________
Unlimited Electric Contractor/Standard Electric Inspector/Traffic Signal Inspector/Highway Lighting and Level One Traffic Signal Installer. I know you believe that you understand what you think I said but I'm sure you realize that what you heard is not what I meant. |
|
#6
|
||||
|
||||
|
Check with your local POCO. Why arn't they supplying you?
__________________
Unlimited Electric Contractor/Standard Electric Inspector/Traffic Signal Inspector/Highway Lighting and Level One Traffic Signal Installer. I know you believe that you understand what you think I said but I'm sure you realize that what you heard is not what I meant. |
|
#7
|
|||
|
|||
|
480 VAC Single phase is one hot, one grounded conductor and one EGC. I would think?
|
|
#8
|
||||
|
||||
|
Brian,
One hot, one grounded, and one EGC on a 480 systm would yeild 277 volt, unless I'm mistaken.
__________________
John “For those of us who believe in physics, this separation between past, present and future is only an illusion, however tenacious”- Albert Einstein |
|
#9
|
||||
|
||||
|
It is 480 1 leg to ground.
__________________
Unlimited Electric Contractor/Standard Electric Inspector/Traffic Signal Inspector/Highway Lighting and Level One Traffic Signal Installer. I know you believe that you understand what you think I said but I'm sure you realize that what you heard is not what I meant. |
|
#10
|
|||
|
|||
|
Quote:
A single phase 480:480 transformer, like the OP asked about, could be used to create a 480 2-wire secondary which could then be treated the same as any other 2-wire system.
__________________
I think I have already told you more than I know. |
![]() |