Does anyone know of any specific support requirements for lights fixtures that are not installed in a suspended ceiling system?

Specifically, are there any codes that require redundant support for fluorescent high bay lights in a gym? I looked and haven't found any.

I know it was common practice to provide safety chains for pendant metal halide lights, but I'm not sure it was a code requirement. And I'm sure those fixtures weighed a lot more than fluorescent high bays do.
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
I would check with your local jurisdiction. Where are you located?

At the least the support would need to be no less that the weight of the fixture.
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
A client thinks there is a code requirement for two types of support - like a pendant and a safety chain.

I think that was common for MH fixtures that were pendant mounted, but I don't know if it was a code requirement.

And I don't think there is anything similar for fluorescent lights.
 