Results 1 to 4 of 4
Thread: Panel Clearances
  1. #1
    Exclamation Panel Clearances
    I'm installing a baggage handling system at Miami International Airport. The conveyor is approximatley 24" from the concrete wall. I have a 480v 3.5 HP motor disc. switch along with 120v control boxes on this side of the wall. The airport inspector is telling me that there must be 36" clearance. I could probably agree on the switch. but not on the controls. What say you?
  2. #2
    Join Date
    May 2004
    Indiana
    Posts
    1,266
    110.26(A) appears to be the reference you need to study.
    The switch is actually condition 2 (backed by a concrete wall) at 480VAC and therefore 3'6" not 3'.
    If what you refer to as "control boxes" are nothing more than pass-thru or terminations then they might bypass 110.26(A). If they contain fuses, relays, or other control components then 3'.
    A rose by any other name is tax deductible [1978 Wayne Wilcox]
    People who read too many books get quirky. [2000 John Taylor Gatto]
  3. #3
    Thanks pfalcon! I just found it about 10 mins ago, so you are correct.
  4. #4
    You are exactly right! I found it about 10 mins before you replied. Thanks pfalcon