    I was told the conversion for changing kilowatts to btu's was to multiply by 3.4 . So if i have a 5kw electric 240v heater it would be a 17,000 BTU heater. Can anyone confirm this? Thank you.
  2. #2
    Join Date
    Aug 2007
    Posts
    2,754
  3. #3
    Join Date
    May 2005
    Richmond, Virginia
    Posts
    22,835
    In a little conversion app I found, 5 kw is equal to 17,075.9 BTU/hr, in the power converter.
    It also says that 5 kw/hr is equal to 17060.71 BTU, and this is in the energy converter.
    Obviously, one has time in it, and one does not. Therefor, there's no direct conversion.
    Added: But, yes, to your question, for all practical purposes.
    Code references based on 2005 NEC
    Larry B. Fine
    Master Electrician
    Electrical Contractor
    Richmond, VA
  4. #4
    Join Date
    Mar 2008
    Posts
    9
    Thank you for your help!
  5. #5
    Join Date
    Aug 2007
    Posts
    2,754
    to be more precise, the BTU is a measure of energy. The watt is a measure of energy per second. So for a given conversion, a watt would equal a given number of BTUs per second, or BTUs would equal watts times a given length of time.