main panels and sub panel ampacity tables

Status
Not open for further replies.

Volta

Senior Member
Location
Columbus, Ohio
It is all T310.16 (for those types of wires), with an exception of 310.15(B)(6) only for "main power feders", or service-entrance or -lateral conductors, as 120/240 single-phase for dwelling units. Otherwise, stick with Table 310.16.
 